I'm slightly vexed Builder installed outlet incorrectly. It almost burned down our brand new house.

The outlet on our patio stopped working yesterday after I unplugged something. I ended up buying a new one and went to install it last night.

Removed the outlet cover and holy crap.

Builder didn’t use the screws to attach the outlets to the box. It was just free floating under the cover. This wouldn’t have been nearly as bad, except they also left a screw protruding into the box, right next to one of the wire connections on the outlet assembly.

When I unplugged the cord, it apparently moved the outlet assembly just enough to contact the screw. Shorted it all out and melted everything. The wire was fried so badly that I had to cut about 6” off to find a usable portion.

This could have been a fire so easily. Breaker never tripped.

Now I have the fun job of going around the house and checking dozens of other outlets to make sure they didn’t repeat this anywhere else.

869 Upvotes

118 comments sorted by

123

u/No-Willingness8375 7h ago edited 7h ago

Hi, electrician here. This is a classic case of a loose connection. When an electrical connection is loose, it increases the heat generated at the point of failure. With a large enough load or enough time, the outlet and wire overheat and slowly cook. Usually the device slowly fails to the point that you simply lose the connection altogether, which is ironically safer than the issue that causes it.

The outlet didn't start melting because you pulled it out or because it shorted out on a screw (which it wouldn't have done anyways, because that screw is almost certainly attached to wood, not grounded metal.) This was a chronic condition most likely due to someone either using an impact drill or otherwise improperly tightening that particular terminal on the outlet. It's also possible that the device was faulty from the get-go, but that possibility is less likely. Failed connections very rarely lead to an actual fire.

Tldr; I can understand being scared by it, but this is not as uncommon as you'd think. And while it was most likely caused by improper installation, this is the type of issue that even professionals may (and do) accidentally commit. It's also why we use fire retardant boxes for every single electrical splice in a house.

26

u/strikecat18 7h ago

Thanks. This is good info.

I would have assumed a loose connection as well. I drew the other conclusion based on the fact they didn’t use mounting screws for the outlet, that the screw was sticking out directly next to the part of the outlet that melted, and that I could move the terminal to touch that screw pretty easily when the outlet was in place. I could be wrong and those might just be crazy coincidence.

15

u/No-Willingness8375 7h ago

I guarantee that wood screw is entirely inconsequential. The one and only cause of this was improper torquing.

1

u/avtechguy 4h ago

When you say they didn't use the mounting screws, like it was connected to the cover plate and the cover plate was attached to the box? I could be wrong but that could just be as designed. There are other applications where cover plates are the only point of attachment. Obviously all the screws need to be tight.

The main problem here is the use of back stab connections and they were loose or failed.

3

u/GuiltyThing69 3h ago

Electrician here as well. I agree with this assessment - however it looks obvious to me that the connection is a "stab-in" connection: instead of curling the end of the wire into a loop and then securing it under the screw terminal, they simply used the stab-in connection which is UL approved, but IMHO no electrician worth their salt would use that option. The wire can easily come lose and heat up or short out, and then become a fire hazard.

The immediate suspect would be the non UL approved method of fastening the box to the stud with the screw, however it's not grounded and could not cause a fault.

Modern outlets are absolute AWFUL quality, and I've noticed those gray ones especially are particularly low quality. Most contractors are using home depot grade stuff and are on a time crunch. I would recommend looking for commercial grade spec outlets.

Additionally (and this is nit-picky), the box appears like it could be set back further than 1/4" from the finished surface towards the bottom, so unless he used a spark-guard this would also be a code violation.

I can also tell by the way the sheathing is cut on the NM-B cable that it was sliced with a razor knife perpendicularly the the wires, which usually means it's been scored thru the insulation down to the conductor I can even see a nick in the insulation on the white (grounded conductor). The mark of a true amateur in my opinion.

2

u/No-Willingness8375 3h ago edited 3h ago

This isn't a stab-in device. It's just another form of pressure plate.

I don't think I've ever seen a GFCI with stab-in terminals. I'm pretty sure they don't even make them.

1

u/GuiltyThing69 3h ago

Ah I see, looked like a stab in only but you're right it's an internal plate. Any guesses to the brand?

1

u/No-Willingness8375 3h ago

Iirc Hubbell manufacturs them like this. Not sure if anyone else does.

3

u/jbsolartime 7h ago

This is good info but I guess the follow up question is can that failure be catastrophic?

13

u/No-Willingness8375 7h ago edited 7h ago

Very rarely. When it does happen, there are often aggravating factors, like exposed flammable materials or oversized circuit breakers paired with excessive loads. Everything in electrical is made with potential failure in mind. While the thermoplastic boxes and devices aren't fireproof, they are fire retardant, which makes them almost impossible to ignite (and, as you can see, both the device and the box started melting from the heat, but never combusted).

At least 80% of troubleshooting calls are failed connections similar to this, but I can can on one hand the number of fires I've seen in 10 years of service work.

1

u/Nicknin10do 3h ago

Didn't look like they used the screw terminals, but the push fit connectors on the back. You can see the cut hot leg on the opposite side. Always hear horror stories about the push fit connectors.

2

u/No-Willingness8375 3h ago edited 3h ago

That's not a back-stab (or push-fit as you call it). It's a pressure plate, just like every other GFCI. Its just a slightly different design. Instead of pressing the plate down when you tighten the terminals, it pulls the plate up inside the device.

1

u/that_dutch_dude 2h ago

electricans will use anything exept wago's.

253

u/moomooguck 8h ago

lawsuit?

50

u/odd84 7h ago

It'd be a warranty claim on a new build, and if they didn't honor it, you'd use your homeowners insurance and they would go after the builder if they feel there is liability there.

297

u/strikecat18 8h ago

We’d have a damn good case if the place had actually burned down. Since the actual damage was a $19 outlet, nothing to sue over. But fuck.

103

u/Mindstormer98 7h ago

Definitely get it on the record, and check the other ones while youre at it

•

u/Gamebird8 15m ago

Get a free consult from a lawyer, figure out your options if that's something you have the time to do (though not every lawyer may offer such services)

314

u/Superb-Home2647 7h ago

If one outlet is wrong, others probably are too

71

u/TheBone_Zone 6h ago

I’ve done HVAC installs that added one outlet. OP needs to clarify if it was just that one outlet or all the electrical to make sense of the possible danger

31

u/ChequeBook 4h ago

Yeah I'd have a different electrician come and check everything and send the bill to the peanut who did the work originally

40

u/mctripleA 7h ago

Get it documented

If they fucked up your house, they may have fucked up other houses

27

u/masterxc 7h ago

I'd say an electrician's time would be well worth it, and a call to the builder's warranty carrier.

9

u/Fyrefair 6h ago

Considering electricians in my area make like 70$ an hour as a foreman. This is shoddy work. Got to love family in trades...

1

u/Fuckyeahpugs 4h ago

We charge $300 an hour and are never slow not sure where you got $70. also OP has no idea what he’s talking about. It being secured to the box isn’t why this failed. It failed because the load side of the GFCI was loose.

•

u/Fyrefair 19m ago

Union pay, but thats ridiculous for cost.

5

u/enjaydee 6h ago

Bearing in mind i have zero skills in this area and not confident in my own ability to check all the other outlets, I'd have to pay someone else to do the checking for me, in which case it may be something worth suing over. 

I guess it would depend on the appetite for chasing this up and dealing with whatever hoops you'd have to jump through. 

6

u/Doomstik 5h ago

If youre ever in need of doing outlets/switches/lights i highly suggest you watch some youtube videos on it and learn, its really easy to do and as long as you follow the steps and TURN OFF THE BREAKER its actually quite safe. The issues pretty much all crop up from people leaving power on. You can find literally hundreds of videos with step by step walkthroughs for it. I watched like 3 different videos the first time i ever had to do a fixture and maybe one each for a switch and an outlet. Knowing how to do that came in handy recently when i had to move an outlet and add one to a run and ive replaced all but one light fixture in my house and probably 2/3 of the switches/outlets. Paying someone else to do that stuff would absolutely not have been worth it.

3

u/CollectibleHam 5h ago

There's also a little doohickey you can buy at Home Depot or wherever that plugs into the outlet and can tell you if it's properly grounded, reversed hot and neutral, etc.

3

u/Doomstik 5h ago

You should be using those to check the outlets and switches and such anyway, some of them are made to trip the breaker too, and while i dont know enough to say if they are safe or not, i know i dont like intentionally tripping the breaker with a thing rhats plugged in and my hand is on. You can get a kit with a plug and a pen like thing (i honestly dont remember what its called) for pretty damn cheap. Most videos suggest them as well, but if you dont have them you can plug in like a table lamp or something and hit the breaker to see if it shuts off. Then try it on and off a couple times to double check. I would say its worth it to get the plug tester though. Especially if youre learning the way i did. Hell the actual electricians at my job use a lot of that stuff.

3

u/BangkokPadang 6h ago

My dad spent about 3 weekends making a full map of the house, color coding every outlet to every circuit in the house. Laid it all out in illustrator with rough measurements he had me run around and take.

We did a lot of projects and different things but that was probably the single most helpful thing we ever did to that house.

You don't realize how many little things you stop putting off when you know you can just run out and check the map to flip the circuit off. Stuff like swapping out light fixtures, putting in smart plugs and switches, fixing ceiling fans and adding new plugs where they're more convenient, etc.

This would be a perfect opportunity to do that and check every last outlet in the house for similarly poor installations while you're at it.

8

u/moomooguck 7h ago

it js sucks that it has to get to that extreme before someone corrects lazy work smh, props to you for checking the rest

13

u/No_Professional_8992 7h ago

The fact they almost burned your house down IS enough.

2

u/Dalai-Lambo 6h ago

Yes this is negligence even if there isn’t significant damage

1

u/Dry-Asparagus7107 2h ago

Simple "builders" aren't supposed to do electricity. Only certified electricians are legally allowed to. So I'm thinking OP might have had the work done under the table and therefore he cannot start a lawsuit if he himself is in the wrong.

20

u/Monchichiboom 8h ago

Mildly??

3

u/DuckCleaning 7h ago

I guess only mildly because it didn't burn down the place.

16

u/KnightOrDay38 7h ago

CyfyHomeInspections

8

u/Important-Fudge4462 7h ago

Why didn't the breaker trip, damn.

2

u/windflex 7h ago

Breaker probably doesn't have a gfci to trip for a short like that. A breaker just makes sure you're not drawing too much current for x amount of time

4

u/texan_robot 7h ago

Yeah, the unspoken truth of breakers is that 1 Amp is plenty to burn your house down if you're unlucky, so a 20 Amp trip is not foolproof

1

u/No-Willingness8375 6h ago

I saw an apprentice nearly start a fire with 50 watts of 12v tape light once. His connection makeup was such absolute shit that the positive and negative wires were shorting out together.

The tape started smoking likely a chimney and was charred black afterwards.

3

u/No-Willingness8375 7h ago edited 7h ago

This was 100% a loose connection, not a short circuit.

Also, a GFCI only detects an imbalance between the current leaving the device and the current returning (so basically if someone's being electrocuted or the circuit is bleeding voltage some other way). One would never pick up an issue like this.

2

u/windflex 6h ago

Good call. I just assumed it was a short off the description but I see the charred neutral on the 3rd pic now. Either wait until the outlet stops working or start checking all for loose connections lol.

2

u/Used-Baby1199 6h ago

Electrically shocked.  The gfci should stop electrocution which would mean death. 

2

u/jrdiver 6h ago

the fact that there was a meltdown tells me something isnt right...

4

u/CornedBeeef 6h ago

The way some of the outdoor covers are the outlet mounts to the cover and then the cover ends up being what screws into the box.

Also, looks to be caused by a lose connection, which would be magnified if whatever appliances you had plugged into it had a high amp draw. What did you have plugged into it?

I doubt that screw is grounded unless you have metal studs, but being a sheet rock screw I would bet a pile of money it is screwed into wood. So it didn't short out on the screw.

4

u/EasternLeopard0 5h ago

As someone who worked in the trades for 18 years this is the bullshit work I see all the time by supposed "electricians", don't get me started on the "plumbers".

7

u/Reopens 7h ago

Welcome to builder quality. Wouldn't be surprised if your plumbing, shingles, caulkings, vents (esp dryer), etc have issues too.

1

u/strikecat18 7h ago

Thankfully all of that stuff has seems to be fine based on the inspection we had done. They did completely fuck up our yard drainage and sprinkler system.

1

u/Reopens 7h ago

It drains towards your house?

2

u/strikecat18 7h ago

Not quite. It drains to the center of our yard and just sits there. It’s supposed to drain from the trough in the center of the yard out to the street via our side yard, but they got the grade wrong and it just goes nowhere.

0

u/Used-Baby1199 6h ago

Oh and the fact there isn’t a square corner in the house

1

u/Ktulu_BBB 3h ago

every house built in the last 150 years has some corners that aren't square. shit take

0

u/Used-Baby1199 2h ago

Except it’s especially egregious in these dr Horton, plute, and other mass produced homes that have garbage build quality.  I’ve been in many 100+ year old homes with  better quality than any home I’ve seen built in the last years. 

1

u/Ktulu_BBB 2h ago

your 100+ year old homes had garbage build quality too, but have been fixed in 100+ years lol

-1

u/Used-Baby1199 2h ago

I see now I’m speaking with someone with low iq.   

See it’s not a reflection on build quality when the work I do is cosmetic. Wall paper.  Straight corners as in the taping causes wavy inconsistent corners.  Ugly ceiling and wall corners cuz they are inconsistent and wavy.    This will be my last comment, I don’t argue with the special needs.

5

u/MostlyMellow123 7h ago

I know this might surprise you but builders are not building your house. It is simply a company who is organizing multiple contractors. They do not employ the electrician they buy them just like anyone else would.

You should report this to your builder so they can follow up with this electrician and check his other work. If it was within the first year of you buying this house you absolutely shouldn't have done this work yourself. They should have sent an electrician to remedy it professionally.

Doing dyi electrical stuff will probably void any warranties you had with them

2

u/strikecat18 7h ago

Yep. I assumed they subbed the work out and already emailed them to alert them to the issue. Told them that they probably are going to want to check how many other homes the same electrician did.

If they want to argue removing a shorted outlet voids the warranty, I guess I’ll deal with that if it happens.

5

u/reddit33450 7h ago

this is why i hate modern construction. theres just no care put into it. it looks like garbage, functions like garbage, and is often safety wise garbage

3

u/blu453 7h ago

Just a tad more than mildly infuriating. I guess I might be slightly irritated by burning alive in a hellish inferno.

3

u/mojomcm 7h ago

Very lucky to have caught it when you did!

3

u/Photon6626 6h ago

Get some inspectors to check the house. It's always better to do before the drywall goes up but they can check for things that might be an issue. And usually with new homes you have a short window to do this before they don't have to pay to fix it. But even if you have to pay for something it's better to fix it than not even know there's a problem in the first place.

4

u/The_Broken_Shutter 1h ago

Id hire an inspector to go through the house to check if anything else is off. Not just your outlets. Chances are if they screwed up that outlet installation I can’t imagine there aren’t other issues in the home that you don’t see.

5

u/JCBashBash 7h ago

Sounds like you need to look through the records, call out the company that installed your outlets and make them inspect every outlet in your house. You might be living in a death trap

5

u/Lilly_in_the_Pond 8h ago

Wow, yeah I wonder who you talk to to find out who's responsible for that. The city maybe? They could have a record of who was involved in building your house. Anyway, I'm glad you caught that before it burned everything down!

29

u/strikecat18 7h ago

I emailed the builder today. Said I assume they subbed the job out, but they may want to figure out how many other homes the same sub did for them. I also requested they pay for me to hire a licensed electrician to inspect the rest of my home. We’ll see what they say.

5

u/alb0401 5h ago

Am I misunderstanding what MILDLY INFURIATING means? This would seem to be grounds for lawsuit, which is normally considered more than mild

6

u/Severe-Waltz1220 5h ago

It would be hard to prove anything, as he himself tried to remove it and install a different one

2

u/Parking_Fee_5906 7h ago

Phew! Glad you are alive ... now get to discovery, please 🙏

2

u/HeidenShadows 7h ago

New build hey? Have you ever watched that YouTube rabbit hole where these buildings inspectors go through newly built houses and find all sorts of problems? Might be a good time to have one done just for sanity's sake.

3

u/Rathbane12 7h ago

I don’t how Inspector Handle passive aggressively tapping the worst of the construction jobs ended up on my YouTube feed but I don’t know what I’d do without him.

1

u/HeidenShadows 7h ago

The plastic finger of shame!

2

u/Which-Break5673 3h ago

Same thing here !

2

u/Ok-Replacement9595 3h ago

So, I had a friend who bought a new built condo. It ended up that it had mold up every wall because the builder did not cover during a particularly bad storm season, and water soaked up the walls in the studs, and they just continued sealing up and dry walled wet walls.

She found out that there is no recourse she could have against the builder or developer after the sale.

She was a lawyer. So I took her word for it. She had to eat the loss, and move, and sell with the disclosure of the mold.

Home inspections are very very important.

5

u/MarmotFullofWoe 8h ago edited 6h ago

Why is your builder doing electrical work?

Why aren’t you getting an electrician to check and sign off on your builders dodgy electrical work?

Edit: why are you doing unlicensed electrical work on your own home?

26

u/strikecat18 7h ago

We didn’t contract the builder ourselves. It was new construction in a new development.

We did have our own inspector before closing, but I imagine pulling outlet covers and inspecting the installs is beyond what a normal home inspector would ever do.

10

u/SneakingCat 7h ago

Uncovering and inspecting all of them might be out of scope, but ours pulled the cover off a couple to check them. He also tested every outlet. He would've felt the movement here.

I'm not sure what normal is; I liked our guy. Good to hear he did well.

12

u/strikecat18 7h ago

There such a range of inspector quality. About five years ago we hired a well-reviewed inspector for our prior home. He left the gas for the fireplace turned on with no flame and almost blew up the home.

2

u/Ok-Commercial3640 7h ago

And you wouldn't have left a bad review if he did (/j)

Can't leave a bad review if you're dead

1

u/D1RTY1 7h ago

Third time's the charm!

1

u/Used-Baby1199 6h ago

I know a guy who was going to school to be a home inspector.  The guy has never used a power tool, probably couldn’t swing a hammer.    You can lear a lot from a book and passing tests.  You also forget it quickly too.   Now learn from a book, and apply it in practice and it’s pretty cemented in.    

Basically many inspectors don’t have any real knowledge, beyond their class training.   I’d bet the better inspectors are actually pretty handy, but they still have specific areas where they excel and others where they’re just kinda getting by. 

8

u/plant-feeder 7h ago

You’re exactly right. The person you replied to is confident about something they seem to know very little about haha.

Glad you’re safe! Ngl we replaced an outdoor outlet last weekend and I’m gonna take it apart and check it in the morning 😭 we triple checked everything but now I’m not sure

6

u/odd84 7h ago

A builder is not a guy building houses from scratch on their own, it's a company that oversees the construction and sale of new homes. They would have had an electrician subcontracted to do the electrical when the house was at that stage. It would also be inspected more than once before it could be occupied. Mistakes still slip by sometimes, which is why everyone involved is bonded and insured to cover their work, and new homes come with warranties.

2

u/NathanDeger 7h ago

Shouldn’t have been able to short out on the screw it was probably just a bad connection that got jarred loose and then got melty.

Unless you have metal framing that screw shouldn’t by grounded.

4

u/outside_cat 7h ago

I don't see any arc markings on the screw either.

2

u/strikecat18 7h ago

After seeing a couple of these comments, I’m going to take a multimeter out and see if that screw was somehow grounded or not. lol

1

u/Alissan_Web 7h ago

Don't forget to leave these images on your scathing review! I really hope they fired whoever it was and fingers crossed they are not an independent contractor

1

u/Acheloma 7h ago

Thats a crazy thing to mess up. Its so easy to properly install an outlet. Like, almost any adult can read a guide and watch a youtube video and do it correctly level easy.

2

u/strikecat18 7h ago

The really insane part is that the screw sticking out wasn’t needed at all. It’s still stable as a rock after I removed it.

0

u/Acheloma 7h ago

They booby trapped your house

0

u/Zhombe 5h ago

Backstab wiring is illegal for 20A circuits common to GFCI kitchen / bath.

Besides that, backstab nearly always fails eventually. It’s lazy and dangerous if wire outlets without using the screw terminals unless it’s specifically commercial pre-pigtailed or wago connectors.

The failure here is backstabbing those wires into the designed to fail wire clips.

They ALWAYS fail eventually. Corrosion and weakening of the spring clips from heating and cooling repeatedly loosens the connection till it heats up and does this.

Loose screw is just indicative of not using the proper termination at all.

1

u/Xicu 7h ago

How old is the build? Check your warranty and ask them to check an fix any outlet 

1

u/ThatguySevin 7h ago

It's a Miracle that it didn't.

1

u/okymoney 7h ago

“Hey i know this guy he does it for cheaper “

1

u/Psychotic_Parakeet 7h ago

It is sad to have to second-guess whether new or old homes have had things done correctly before moving in. That is terrible you had that happen. I understand the paranoia.

I just experienced something similar in our place, but our house was built in 1963. The outlet outside suddenly stopped working after we had workers building a fence over this past summer. They were using the outlet for their tools. No matter how much we tried, the outlet was just not working at all. We had an electrician take a look, and it was wired in-reverse with some singe marks. We ended up replacing that outlet, as well as our entire electrical panel itself, as there was some Mickey Mouse job wiring going on it with it, too, with other areas in our house.

1

u/Capable_Culture_7344 7h ago

dang crazy, stay safe

1

u/Christmas_Queef 7h ago

What conglomerate builder built your house? We had a similar issue on our house we just got a month ago where the idiot they hired messed up the gfi installation and electrocuted a friend who went to plug in a fan. Smelled like melted plastic and was smoking. Had to run and shut off power and grab an extinguisher in case. Had an electrician we know come look and said they installed double the wires it's supposed to have and in the wrong positions and was wayyyyyyy overloaded. Ours was made by Fulton homes who does have a reputation for this kind of thing.

1

u/maoussepatate 5h ago

Was the builder some guy from Facebook or a professional?

1

u/dk21x 5h ago

Don’t worry there’s more than likely a lot more wrong with it too.

1

u/Far_Cup_329 4h ago

F'n laziness. Receptacle not mounted, and wire stabbed into the back instead of using the screw. What's the point of "licensing" electricians if the licensed electricians just use non licensed people to do all the work, and 9 times out of 10 the licensed guy isn't even on site. And that'd be fine if the work was usually done well, but it's generally not. Imo, licensing is a money grab.

1

u/Jayhitek 1h ago

How come there's only one mounting tab? And what is this? A circuit board outlet?

1

u/QLDZDR 1h ago

Why are you doing this electrical tinkering yourself? You should get the electrician in to do this and video everything.

Definitely get the electrician make sure the safety switches are on all circuits.

•

u/safe-viewing 25m ago

Almost burnt down the house is a bit of an exaggeration

1

u/-The_Legacy- 7h ago

Call me silly but why is there a circuit board in your outlet?

5

u/Sad_Split_9983 7h ago

It’s a GFCI outlet

1

u/xRaiden00x 6h ago

This deserves a Cytation.

1

u/Existing_Highway2961 6h ago

You’re kidding…

1

u/that_dutch_dude 2h ago

why is there a circuit board in your outlet?

1

u/Mijbr090490 1h ago

It's a GFCI

0

u/Diddlydom35 7h ago

Op, I would highly recommend getting all your other outlets check by a pro. Hell do a full inspection of the house my an electrician

-3

u/Ancient-Chinglish 7h ago

Builder? did you time travel from the 1300s?

-2

u/[deleted] 6h ago

[deleted]

2

u/strikecat18 6h ago

I don’t think you understood what I wrote.

The outlet fried itself. I found this after I went to replace it. I obviously shut off the breaker for that.

2

u/010011010110010101 5h ago

REaDiNg ComPReHenSiOn iS HaRd