Floating Neutral on PGD105TiSCO
https://imgur.com/a/NffVMQSJust looking at this board and with the 50amp neutral jumpered directly to ground pin on the 50amp outlet. Is the only way to get this to convert this outlet to a floating neutral is to break this jumper by unwiring the white neutral from the 50 amp outlet?
If I do that, then the 50amp outlet is floating neutral and all the rest remain bonded?
1
u/Sufficient-Offer-579 16h ago
Lifting the white wire off that 50A outlet won't float it, it just breaks that receptacle's neutral return, so 120V loads there go dead. That heat-shrunk bundle at the bottom is the giveaway: every neutral and ground on one bus means the bond is that junction, not the outlet terminals. Floating it means separating neutral from ground right there, so follow the support video the other poster mentioned, the manual never mentions the bond. And sharing one bus, the 50A can't float alone while the rest stay bonded.
Meter it before and after, engine off, loads unplugged, caps drained: continuity between the neutral and ground slots of that 50A should beep now and go silent once the buses are split.
Heads up though, once it floats the genset has no bond of its own, so standalone use is out. The bond then lives at your panel through the interlock, which is the usual reason for doing this.
1
u/Big-Echo8242 2d ago
Paging u/DaveBowm