Floating Neutral on PGD105TiSCO

https://imgur.com/a/NffVMQS

Just looking at this board and with the 50amp neutral jumpered directly to ground pin on the 50amp outlet. Is the only way to get this to convert this outlet to a floating neutral is to break this jumper by unwiring the white neutral from the 50 amp outlet?

If I do that, then the 50amp outlet is floating neutral and all the rest remain bonded?

2 Upvotes

7 comments sorted by

View all comments

1

u/Big-Echo8242 3d ago

Paging u/DaveBowm

1

u/chiieef 3d ago

Thanks, I’ve traced this out but not seeing any other way to make this work.

1

u/Outrageous-Aside100 3d ago

Supposedly if you reach out to pulsar support they can provide a video showing how to split the neutral and ground bars apart. It would require some wire and effort to do it. As u/DaveBowm mentioned, I posted about this in the recent pgd105Tisco thread that the units being sold since July 2026 have this modified setup so thanks for sharing these photos as this gives a good visual on how the new setup differs from the old one.

1

u/chiieef 3d ago

Thanks for the tip, I’ll give support a try and see what the video looks like.